Earlier quoted context omitted.
Yes, something similar happened in the UK a while back. Full info here: https://www.ofgem.gov.uk/sites/default/files/docs/2020/01/9_... Key points that started it were (you can see the chain of events in the doc): 2.4.1. At 16:52:33 on Friday 9 August 2019, a lightning strike caused a fault on the Eaton Socon – Wymondley 400kV line. This is not unusual and was rectified within 80 milliseconds (ms) 2.4.2. The fault af…
Curious question for someone familiar with power at grid-scale -- How granular is load shedding? And how is this measured / tracked? In my head, I'm thinking of generators/plants, connected by some number of lines, to some amount of load, where there are limited disconnection points on the lines. So how do grid operators know what amount of load will be cut if they disconnect point A123 (and the demand behind it) vs…
When yhe time comes, you just shed enough "buckets" to stabilize. Load shedding is not a precise task, when you're at that point, you'd rather load a few more megawatt and be safe, than play with the limits and be sorry.
> So how do grid operators know what amount of load will be cut if they disconnect point A123
Opening a line within the grid isn't used to shed load, as the grid is mainly redundant. It's used 1) to protect the line itself (either by letting it trip, or by opening it preventively), or 2) to force power to flow differently through the network, by modifying its impedance. Opening a line from the transport network is not a way to load shed.
In this totally random example [1], opening the line A-B increases impedance in the right part of the network, forcing power to re-route through the left part, and reduces the load on another line in the right path that was overloaded.
[1]: https://excalidraw.com/#json=5l8OS96Wdke6l9YEClQt8,NJ-r2PtiE...
> Or is there continual measurement? (e.g. there's XYZ MW of load behind A123 as of 2:36pm)
The network is, indeed, monitored continually, and we do have potential network equipments failure simulations every few minutes, with contingency plans also simulated to make sure that they work in that particular case. This way, when shit hits the fan, we at least have a recently tested plan to start from.