Nearly 2 years ago, we had a small tornado come through, taking out our electricity for a week. During that time, it was snowy and the outdoor temperature was well below freezing (it reached about -10°C (12°F) at night).

Keeping my family warm was a real struggle that week. The next spring, I went to Costco and bought a big tri-power generator and wired up a generator interlock on the electric panel. Now if we lose power, we can run the natural gas furnace & blower with no problems. I can also power the generator from my home's natural gas supply instead of making frequent trips for gasoline.

So I'd say heck no to swapping the natural gas furnace for a heat pump. I'd much rather use natural gas to power both the generator and the furnace/blower than risk needing more electricity to keep my family warm than my setup can handle.

Re: Harnessing America's heat pump moment

#72

Cool to see a Heat Pump article near the top of HN! I'm the founder/CEO of Quilt ( https://www.quilt.com/ ), which is mentioned in the article, and a decade+ daily reader of this fine site. At Quilt we've run the Nest playbook for ductless heat pumps as our first product. The plan is to do what Tesla did for automotive to the built environment infrastructure category (HVAC, plumbing, etc) and create the first major A…

Hey Paul! Good to see ya on here. I'm in a Facebook group of small HVAC contractors, and recently there was a conversation about who is installing heat pumps vs traditional ACs and furnaces. I was thrilled to see that most were saying that they are moving a lot of their business toward heat pumps. Of course, there were a few that were stuck in their ways and were "gas or die" type people, but it's exciting to see the ship slowly starting to turn. There are more and more heat pump forward contractors coming online every day, and it's great that we can team up with folks like you pushing the hardware forward. There is so much work to deploy these systems, and winning is going to look like all of us working together!

Re: Harnessing America's heat pump moment

#73

It’s very hard to say whether heat pumps are cheaper than NG for heating. I pay about $0.25 per 100k BTUs which is about 3kWh. 3kWh costs about 50 cents. As long as the COP is above 2, it’s cheaper to run the heat pump. Once you factor in an electrician and pipefitter for installing a heat pump, plus the cost of the heat pump, refrigerant, and furnace coil, I’d imagine you lose money in the long run. If you then addi…

Its not hard to say at all, the math can be done pretty easily based on your local electric and gas rates, and most people who go for a heat pump already need an air conditioner for summer.

The math actually works out in many places unless you have cheap gas and expensive electricity. Its also better then to burn the gas at a power plant at 60% efficiency then 300-400% efficiency at the heat pump than pipe and burn the NG at 80% efficiency in your furnace.

Re: Harnessing America's heat pump moment

#74

Earlier quoted context omitted.

Just checked the spec of mine at -10degC. It's a bit over 3.

That’s +15F, what’s the COP at -26C?

Whoops, my bad when doing the transformation. It won't work that low, only down to 20degC and at that point it probably approaches 1. Lucky me, the temps never dropped to under 19degC in the last 20 years in my area. So I'm probably going to be fine.

Re: Harnessing America's heat pump moment

#75
post #33

People are reluctant to install them because they don't work as well as the good old boilers we'd be replacing. I'm not saying they can't, and I'm not saying that there are zero models out there that work. But in practice, a lot of us that have interacted with heat pumps have the specific experience that they get anemic as the temperature goes down and eventually become unable to do much of anything. I live in the mi…

This is such a weird tale to hear. I heat my 2 story 147m2 house in Sweden with a single heat pump and it's downright cosy down to -10C. I have noticed that my office, which is located at the furthest possible place from the heatpump, tends to get a bit chilly when outdoors temperatures fall below -10°c. usually a blanket is enough to keep me toasty, but on the rare occasion that it gets real cold (below about -15°c), I have a fireplace to save the day. That fireplace actually gets used more for the cozyness of a fire than it does for actual need of heating, but it does help on the worst days of Scandinavian winter.

All this to say: if your pump can't handle +5°c, I wonder if you got scammed or if there are other factors at play? Is your house insulated at all? Do you keep your windows open throughout winter? Your experience is so different from mine it's hard to believe we're even talking about the same technology!

Re: Harnessing America's heat pump moment

#76
post #33

People are reluctant to install them because they don't work as well as the good old boilers we'd be replacing. I'm not saying they can't, and I'm not saying that there are zero models out there that work. But in practice, a lot of us that have interacted with heat pumps have the specific experience that they get anemic as the temperature goes down and eventually become unable to do much of anything. I live in the mi…

I just wrote a big thread yesterday responding to someone with similar concerns to yours (https://bsky.app/profile/shreyassudhakar.com/post/3m3w3nra2h...). Copying it here if it's helpful to other folks. FWIW, the challenges you are facing seem to be grounded in bad design and application, which happens more than it should and really sucks. We need to move the bar much higher for the contractors installing heat pumps. Here's what I wrote on that thread:

This is why contractor & homeowner education are so so so important to get this energy transition right! I always hate to see reviews like this from folks that have installed a heat pump.

It’s almost always a combo of poorly communicated expectations & installer issues.

A few thoughts…

1) “Air doesn’t come out hot” is a common complaint. It’s by design! You don’t need scalding hot air to have a comfortable space. If you’re targeting a 70 degree setpoint, even 80 degree air will get you there eventually. Heat pumps work best when you let them run - they soak the space with heat.

Your furniture, walls, floors all equalize in temp and radiate heat. A totally different form of comfort than standing in front of a vent that blows hot air at you for 5 minutes and then shuts off!

2) AC doesn’t reduce humidity as well. Unfortunately, this is a classic problem with oversized heat pumps. The key to dehumidification is runtime. A well sized system will run for longer, which will pull the humidity out of the space. If the system is too big, it’ll cycle on and off & not dehumidify.

Your contractor should be do load sizing calculations to determine the size of your heat pump, not using rules of thumb or matching the size of the existing equipment! The very best contractors use performance based load calcs, where they look at your past energy bills to size your new system.

3) Supplemental heat runs a lot - this SUCKS. Electric resistance heat is really expensive to run. It really should be something that comes on for emergencies, if ever. Definitely not regularly.

Many contractors set the temperature where the supplemental heat kicks on way too high. You could be running the heat pump (which is way more efficient) to a much lower temperature, but it’ll switch to expensive aux heat instead. Fortunately, the fix to this is simple - just a thermostat setting.

In other cases, they’ll install a cheaper mild climate heat pump in a truly cold climate. This might save money up front, but it’ll kill you in operating costs when you’re paying 4x as much as you could be in the middle of winter to heat your home. The lowest bid could cost you in the long run!

PS - this homeowner later chimed in that swapping the thermostat helped reduce their electricity bill roughly $30/month! A lot of heat pump issues actually boil down to a poorly configured system. Choosing the right contractor is probably the single most important decision you'll make when you get a heat pump installed.

Re: Harnessing America's heat pump moment

#77
All this push to electrify everything makes me nervous, as it effectively centralizes a lever that someone evil enough could use to coerce the general public in unsavory ways.

I'm doubly suspicious of areas that combine mass-electrification with reducing availability of the most reliable alternate source of electricity (i.e. generators). California in particular is pushing to make generators increasingly hard to obtain.

Re: Harnessing America's heat pump moment

#78
post #22

When I needed a new air conditioner I looked into heat pumps. 3x the price.

That seems really weird, the only real difference is a reversing valve that costs a couple bucks. A heat pump is an AC, it just can be run backwards to produce heating as well. In cooling it's literally the same thing.

I'm no expert but the difference in the real world is more than that (though am doubtful about 3x the price) . The delta-T between heating and cooling is significantly greater in most places so you need a bigger system. You also need things like the ability to de-ice.

Re: Harnessing America's heat pump moment

#79
post #33

People are reluctant to install them because they don't work as well as the good old boilers we'd be replacing. I'm not saying they can't, and I'm not saying that there are zero models out there that work. But in practice, a lot of us that have interacted with heat pumps have the specific experience that they get anemic as the temperature goes down and eventually become unable to do much of anything. I live in the mi…

Well

Mitsubishi sells heat pumps that produce 14kw of heat output all the way down to 5f at a COP of 2.3.

Resistive heat has a COP of 1, by definition.

Do you know the size of your oil burner? It's likely over 20kw output.

It's not that pumping heat cannot work sufficiently at cold temperatures, it's that you are expecting the electric car rated 100 horsepower to go as fast as the gas car rated at 300 horsepower.

An oil burner sized to the same output as the heat pump also would not keep up.

If you installed two of those Mitsubishi heat pumps (which would require two independent 240v circuits), you would be at 28kw output and would not need resistive heat strips. These units also claim 75% rated capacity at -13f so that would be about 21kw of heat output even when very very cold.

If your resistive heat strips activate at any point other than extreme weather events or emergencies, your "system" is not sized properly. They are a massive waste of power and money.

A big part of the problem is that the contractors who are essentially the point of sale for these systems are just obscenely dumb about them. They will sell you utterly undersized units or sell units that aren't rated for cold, as well as just install things so poorly that they drain condensate into your walls and cause mold issues. They had similar problems with Oil burners, but at least those they tended to upsell bigger systems so their ignorance didn't matter. They seem very bad at doing the planning or design required to actually spec out a system, so you have to be your own engineer.

>and that is what the industry needs to work on.

I don't know how the industry is supposed to force contractors to read their very very clear documentation, or follow the very clear instructions (of boiler manufacturers no less) of "You must measure heat load to accurately size a heat appliance".

Re: Harnessing America's heat pump moment

#80

Earlier quoted context omitted.

I guess I lucked out; our house had a (very old) whole-home (that is, ducted) heat pump system for heating and cooling when we moved in. When it was time to replace, our local contractor knew exactly what we needed. They even do mini-splits, had we wanted one.

Do newer ones somehow not need ducts? Edit: (or so you mean mini splits?)

No, no ductless magic without mini splits. I feel like a lot of people refer to heat pump systems interchangeably with ductless mini splits, so I wanted to clarify that. Maybe that's just an issue with the people I speak with, though.