Earlier quoted context omitted.
If you don't bond neutral and ground at the main, it's still bound at the transformer. That would be a pretty good trick. The transformer is outside my house on a pole. Two wires run to it, the hot and the neutral. The "ground" doesn't leave the house. (Other wiring schemes exist, but this is standard USA residential.) [EDIT: brainfart, see helpful correction below. still no "ground" at the pole...]
> Two wires run to it, the hot and the neutral Standard US residential is 240V split phase, with two hot and one neutral conductor from the transformer. So three wires, minimum. Unless you have a very old feed.
Why we ground electrical systems (2015)
61–70 of 120 posts
Re: Why we ground electrical systems (2015)
#62Re: Why we ground electrical systems (2015)
#63"Since the ground-fault current path has inherently much higher resistance than the neutral wire, the amount of current flowing through the circuit jumps enormously during a ground-fault." This is incorrect (probably a typo) - the GFC ensures there is a very low resistance path to source, which ensures a current spike that is sufficient to blow the fuse.
Yeah, that was a typo on my part. I didn't notice it at first, and it's now been so long since I posted it that I would feel disingenuous editing it. I think someone pointed out the typo in the comments.
It's perfectly okay to ensure your text is communicating accurate information - in fact leaving it may undermine your explanation as certain folks will focus on the error (or others won't notice it and learn something incorrect).
Re: Why we ground electrical systems (2015)
#64Earlier quoted context omitted.
> Am I wrong in thinking that all electricity is flowing back into earth? Yes, sadly, you are wrong. But it's not a strange error. Electricity always flows in a circle(circuit). And, in fact, in medical devices, transformers are often used to completely isolate devices from the line that they are plugged into. Electrons on the device side of the transformer will NOT try to flow back into the line side or an earth. Th…
When it comes to AC (even discontinuous DC), closed loops are not necessary for current flow. A basic example is a capacitor, which can permit current while it builds up an electric field between is plates. A related example is an antenna, where AC radiates energy that can vibrate electrons in a far away antenna. (Radio telescopes are proof an antenna doesn't need a ground or a closed circuit to receive.)
For example, the current into one terminal of a capacitor does equal the current out of the other terminal. Yes electrons are building up on one plate, but they're being depleted from the other - the net charge of the capacitor remains zero. If this weren't true, differently-charged capacitors would be physically attracted to one another!
If this goes against your intuition, it's because you've become so accustomed to this abstraction of ground which (mostly) lets you forget about the current flow on the other leg of the capacitor.
(In the electronics realm, the use of the term "ground" is much more casual compared to the NEC. To put it in terms of OP, "ground" in the electronics realm is more akin to the "grounded conductor", but alas could actually refer to anything you feel like thinking of as the reference.)
Re: Why we ground electrical systems (2015)
#65I'm actually the person who wrote this Reddit post. I'd never heard of Hacker News before, but someone messaged me on Reddit telling me this 4 year old post just surfaced over here. Let me know if you have any questions about electrical theory or installation, or anything else!
Re: Why we ground electrical systems (2015)
#66Some training videos for pro electricians and US National Electric Code compliance helped me.
Basically, bond everything together if it can carry a charge. Ground that bond at only one place in an electrical service.
More than one "ground" sets up a situation where a potential difference can develop between the various "grounds". Ground Fault detection may no longer work in that case. Which is not good.
(The presentation is weirdly sexist in offhand comments, which I often encounter in trade work of this kind, but I do believe that's changing. Slowly. The USA needs more people who know how to build things.)
Re: Why we ground electrical systems (2015)
#67The details of this also vary based on where you're at. In the US, neutral is bonded to earth at every house I think. In Europe, neutral is only bonded to earth at a local power station.
For example for UK, EU and NZ etc: sockets and pins have a variety of features to avoid touching the phase (live) wire with say a screwdriver or knife in hands of a child.
For example, all new circuits installed in New Zealand since 209 must have an Residual Current Detector (the actual rules lead to multiple RCDs per main power board). This will cut the circuit if someone does manage to touch a live wire somehow (current from phase to neutral doesn't match, because some of it is grounded through your body, and the mismatch triggers the breaker. Wayyyyyyy safer than a fuse!
Re: Why we ground electrical systems (2015)
#68The details of this also vary based on where you're at. In the US, neutral is bonded to earth at every house I think. In Europe, neutral is only bonded to earth at a local power station.
Re: Why we ground electrical systems (2015)
#69This section is plain wrong: "The ONLY purpose for the EGC (or green wire) is to clear a ground-fault (clearing a ground-fault means tripping a breaker or blowing a fuse) in the 'oh shit moments'. It has absolutely NOTHING to do with the ground or the Earth and will work exactly as it is intended to regardless of whether it is connected to the Earth or not." If the EGC is floating, no current will flow in a ground fa…
I'm not trying to be argumentative but you are misinformed. "Floating" means that the system is not connected to ground. That is, there is no system/main bonding jumper. There is no connection to a grounding electrode conductor. This has nothing to do with the Equipment Grounding Conductor, though. I don't know what you mean by a "floating EGC". The entire purpose of the EGC is to bond all normally non-current carryi…
Also the EGC does have more purposes than simply clearing fault current - for example carrying away leakage current from the chassis of something with a switching power supply where the output can't be completely isolated to meet emissions. Ever been shocked by a laptop with only a two-prong AC adapter?
IMO this whole subject is a minefield of disagreements due to terminology, when really all questions are answered by drawing out the schematic of a typical electrical system and looking at the loops (circuits). For instance in the typical ground fault, the fault current returns to the distribution transformer in parallel through all of: your service's neutral, your grounding rod, your neighbors grounding rods/service neutrals, and your other leg of the split phase via turned-on devices. This seems like a lot of unrelated details to memorize until one draws it out.
Re: Why we ground electrical systems (2015)
#70I'm actually the person who wrote this Reddit post. I'd never heard of Hacker News before, but someone messaged me on Reddit telling me this 4 year old post just surfaced over here. Let me know if you have any questions about electrical theory or installation, or anything else!
I then plugged the trailer into an outlet on the side of the house so I could run the air conditioner while I packed it. There was an issue with the brake lights not always working on trailer also. I crawled under the truck to trace the wires (they had been spliced under there before so I wanted to check that area first).
While on my back I rested my forearm against the frame of the truck and then felt a small "pinch". I thought a bug bit me at first, but seeing nothing there, I touched my forearm back again to the frame and felt it again. I realized it was electricity. I had a multi meter handy and I stuck one end of the probe in my mouth and touched the other end to the frame. It read 50 volts a/c. I went and unplugged the trailer from the outdoor outlet and ran it through a window and plugged it into an outlet inside and the issue went away.
So what's up with that?