1. Talk to your hosting providers and make sure they can support 32kW (or whatever max number you need) in a single rack, in terms of cooling. At many facilities you will have to leave empty space in the rack just to stay below their W per sq ft cooling capacity.
2. If you're running dual power supplies on your servers, with separate power lines coming into the rack, model what will happen if you lose one of the power lines, and all of the load switches to the other. You don't want to blow the circuit breaker on the other line, and lose the entire rack.
3. Thinking about steady state power is fine, but remember you may need to power the entire rack at full power in the worst case. Possibly from only one power feed. Make sure you have excess capacity for this.
The first time I made a significant deployment of physical servers into a colo facility, power and cooling was quite literally the last thing I thought about. I'm guessing this is true for you too, based on the number of words you wrote about power. After several years of experience, power/cooling was almost the only thing I thought about.