> oxygen replacing suppressants No, they are a major risk to the employees working there. I would much rather have a data center destroyed by for every twenty years without victims than mandating the user of oxygen replacing fire suppressants.
I understand the concerns you have, however I think there's a good middle ground. Would you consider the following procedure acceptable? - Isolate all rooms with fire-proof doors. - Keep fire supression system at manual. - When fire breaks try to contain (we have 24h watch). - If fails trigger fire supression system. It has 90 second delay and activated per room. - Leave premsises, make the calls. Fire control and su…
OVH CEO Octave Klaba speaking about the incident [video]
91–100 of 143 posts
Re: OVH CEO Octave Klaba speaking about the incident [video]
#92I think the key issue here is that there wasn't a functioning fire suppresssion system in place. Second question: is such a system required for this kind of operation? Maybe?
Re: OVH CEO Octave Klaba speaking about the incident [video]
#93Earlier quoted context omitted.
The problem with water in the same place with high power equipment is that it instantly turns the room into a death trap for any personnel, now everything is potentially live. Also, in the first part of a lithium battery fire, dropping water on them is quite explosive. It will eventually quench the fire but on the short run it will make it worse, filling the room with explosive hydrogen and poisonous lithium hydroxid…
You would be using Halon injection in a normal DC, after sufficient warning to employees to gtfo if they hadn't done that already.
It's fun when someone accidentally dumps the halon system because they pressed the wrong button, and now halon has to be sourced for replacement.
Re: OVH CEO Octave Klaba speaking about the incident [video]
#94If it turns out it's the upses that caught fire, one can't help but wonder if it would be a better idea to house the upses/backup power solutions in an adjacent smaller building outfitted with sprinklers perhaps?
Re: OVH CEO Octave Klaba speaking about the incident [video]
#95Earlier quoted context omitted.
If you're running an IT operation this big, you should have both fire detection units and oxygen replacing suppressants. That should be mandatory. Otherwise, it'd be very hard to contain. Especially when all your servers have RAID controllers with Li-Ion batteries or supercapacitors or other extremely trigger-happy components. Oh, and cooling systems. You're just kindling the fire with it at the beginning.
> oxygen replacing suppressants No, they are a major risk to the employees working there. I would much rather have a data center destroyed by for every twenty years without victims than mandating the user of oxygen replacing fire suppressants.
Re: OVH CEO Octave Klaba speaking about the incident [video]
#96Earlier quoted context omitted.
No. OVH has 27(-1) datacenters.
I'm guessing the other two SBG datacenters took some kind of hit. The buildings are very close together: https://cdn.baxtel.com/data-center/ovh-strasbourg-campus/pho... And the fire looked really hot...like melting steel containers hot: https://pbs.twimg.com/media/EwGqV17XMAMF_wa?format=jpg&name=...
However, they need to bring new power online, as well as bring a new network setup/fiber online to get network connectivity.
Re: OVH CEO Octave Klaba speaking about the incident [video]
#97Are there industry options or methods of wiring to allow for a UPS room separate from the actual rooms the racks are stored in? It's almost tradition to have a rack with UPS's in the bottom and then the rest of the space filled with servers or drive arrays. We wouldn't ever think of putting a tiny backup generator in the bottom of every rack, so why do we put a battery storage system there? Also, with the advances in…
Not all Li-ion chemistries are equal. In particular, the increasingly popular LiFePO4 (LFP) technology has much higher energy density, longer lifespan, improved environmental characteristics, and similar if not better safety characteristics compared to lead-acid.
(Besides sharing lead-acid's very low risk of fire, LiFePO4 also contains no corrosive acids which could damage and short equipment if a leak were to occur.)
Re: OVH CEO Octave Klaba speaking about the incident [video]
#98Earlier quoted context omitted.
I understand the concerns you have, however I think there's a good middle ground. Would you consider the following procedure acceptable? - Isolate all rooms with fire-proof doors. - Keep fire supression system at manual. - When fire breaks try to contain (we have 24h watch). - If fails trigger fire supression system. It has 90 second delay and activated per room. - Leave premsises, make the calls. Fire control and su…
"A common mistake that people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools." -- Douglas Adams
Re: OVH CEO Octave Klaba speaking about the incident [video]
#99Lucky it wasn’t a UPS explosion. https://h2tools.org/lessons/battery-room-explosion
Maybe one day if have a basement and some kind of concrete compartment to put the battery in I'll feel a bit better about it... but even then, not much you can do about gas leakage if that's a possibility with more recent UPSs.
Re: OVH CEO Octave Klaba speaking about the incident [video]
#100Earlier quoted context omitted.
I read his description and literal hand waving as saying that for efficiency reasons, in 2011 they were sort of build like how you'd build a camp fire: convective airflow drawn through and out the top.
Right, this is the OVH “tower” data center design. Here’s a google maps link to the OVH Strasbourg site https://goo.gl/maps/rQjir8byKNwMDZrm9 with (from south to north) SBG1 (a collection of shipping containers), SBG2 (a figure 8 shape), and SBG3 (a box). The idea of the tower design is to take ambient air in through the outside walls, through I think just one row of servers, then into a central void where convection…