For those who dont know why this is important: The loads are slowing down the generators that are burning a well metered amount of fuel to stay at 60Hz. This is a delicate balance since the phase angle must also be spot on. If a generator and the local line disagree on f, phase or V, you have a short circuit. If you lose a large amount of load, your generator will spin up with the excess fuel until the control system…
Would demanding that large spikey users of energy like data centers implement some sort of demand ramping/isolation from the grid in the form of a massive capacitor bank or flywheel generator between them and the grid help reduce the risk here?
However, if a DC detects that the _grid_ is wobbly (voltage or frequency deviations) the DC will disconnect without warning, and switch to its batteries and generators.
The grid complains because it's suddenly lost hundreds of MW of load. For the DC to have isolation capability, it would need a load-sink which can consume roughly the same power as the DC in normal operation, and can take in that load at a moment's notice.
It's a hard problem to solve, and probably better managed at grid-level than DC-level.