We agree return temps should be lower, but to determine how critical this is you need to out numbers on that. In steady state operation at maximum load a difference in return temperatures of 15f is ~1% efficiency. But steady state at maximum load is an extreme situation the average return temperature is well below that theoretical maximum thus an even wider difference is needed for a seasonal difference of 1%. Redund…
As said, at some point you will likely replace your furnace by a heat pump. Then all investment to low temperatures will pay off. A modern gas furnace is no backup for a heat pump, as it also needs electricity. I would recommend a low tech solution like a wood stove for backup. I have one in my cellar. In case of a long power outage I would likely just install this through some open window and do some redneck stuff t…
Particularly in temperatures where the heat pump is at/under 2.0 COP for a few dozen hours per year, an electric boiler makes a great deal of sense. It's almost as clean as the heat pump in the extremely rare times when it's needed for supplementation due to extreme cold temps, can allow for a more suitably sized heat pump to cover the 99% of heating hours [meaning greater efficiency there], is extremely reliable due to its simplicity, is fully automatable with existing controls, doesn't require local gas supply network, and is a pretty good match for a heat pump.