For those who dont know why this is important:
The loads are slowing down the generators that are burning a well metered amount of fuel to stay at 60Hz. This is a delicate balance since the phase angle must also be spot on.
If a generator and the local line disagree on f, phase or V, you have a short circuit.
If you lose a large amount of load, your generator will spin up with the excess fuel until the control system re-establishes the right amount of fuel.
But now your generators are out of sync! No worry, for small disturbances the dissipative losses sync everything up like syncros on a manual transmission.
But the disturance cant be too big!
Rotating machines are big and heavy, so the first line of defense is their inertia. But this is a finite (and precious) resource.
Contrary to belief, renewables, or generally speaking DC, makes things this stability problem worse. They generate large amounts of power while providing no inertia.
You'd think it isn't a big deal since the DC-AC converter can just synthesize whatever is needed. Heck just keep it rigid at 60 Hz with no phase change.
Well the later doesn't work - the rest of the grid is no longer at that phase and frequency so you got yourself a short.
Furthermore, the DC-AC converter, despite their manufacturers' promise, has no good way to establish what f and phase it should be at during a disturbance (and these magic codes are closed source, believe it or not)
Anywho, a large enough loss of load causes the grid to enters into unstable oscillations, causing protective relays to trip causing a zipper effect where the grid goes down.
Now restart will take a few days depending on the energy mix (fastest for hydro heavy)
Long story short - this is not a trivial problem, and the data-centers can't be allowed to just dump load willy nilly.
EDIT: made it clear that the grid killing disturbance is not caused by renewables; not exclusively anyway. Everyone has to play nice or the grid goes down.